排烟阀钢丝绳如果卡阻,会不会影响排烟阀联动开启

排烟阀联动开启的信号是直接给到阀体,还是也需要经过手动执行机构。如果手动执行机构的钢丝绳(线)卡阻了,是否影响排烟口(阀)联动开启

小钟打怪兽 | 2023-12-05 17:29
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

尤里奥洛夫 2023-12-05 23:32 00 [回复]举报

排烟阀的开启是靠模块信号给到电力驱动机构,而手动开启时,更类似于用钢丝绳强制开启执行机构。

在日常工作中,分两种情况:

1、钢丝绳没有油,拉起来很干涩的情况下,是不会影响排烟阀联动开启的,

2、但如果是执行机构卡阻了,那联动时就会影响排烟阀的开启。

安洪全 2023-12-06 08:45 00 [回复]举报

影响

会造成动作不到位

须尽欢 2023-12-06 09:07 00 [回复]举报

当然会,钢丝绳远控排烟阀卡阻就几个点:钢丝绳卡阻、阀体扇叶卡阻。如果钢丝绳卡的话联动也打不开的

阳明心 2023-12-08 08:52 10 [回复]举报

排烟阀联动开启的信号是直接给到模块,模块控制执行机构脱扣后释放钢丝绳,然后开启排烟阀,但当钢丝绳卡死后,钢丝绳无法释放,导致排烟阀不能正常打开。